The good news is I finally got some hard facts about the great duct debate, I have demonstrated that 315 mm ducting does not interfere with the fire detection system as per the recommendation of the FIA, and I have also demonstrated that one 315 millimeter duct coupled with the fan we acquired from an urban tomato farmer comfortably meet the 2000 cubic meters per hour specification requested by the metal tecs.
So as soon as Shaun has built the new box for metalworks extraction fan we can install it hopefully before next weekend.
315mm duct set at a height that allows it to pass over the top of the table saw extraction with a five millimeter clearance.
On the plus side I’ve moved on from doing my calculations on the back of a fag packet to doing them on an old piece of scrap wood. I think that’s an improvement maybe one day I’ll graduates do using a spreadsheet