Hey Hanry,
Huge thanks for your reply, appreciate it!
Nice to hear about your partner, the Charity is Care4Calais.
Thanks for your contributions, very valuable.
Definitly get your point about the walkies, def something to think about.
I like the box trailer idea…currenlty the generators they use are 80kg, which are lifted by several people in and out of vans, i wince a bit and I think everyone could do without that. I remember definitely one van has a towbar. I could check with them though.
They currently use a load of extension cables mounted on long wooden boards, if it rains they use tarps, and plan to get gazebos. The waterproof box trailer idea is great solution.
Looking at how much power they need, I think 5v is a good idea, and means everyone gets a fair share. Would you say 5v at 2A is good to go off?
Very kind about storing the box trailer, appreciate that.
Cost is also something to bear in mind, as they’d have to fundraise for it. They’d also want to run a pilot, I think how this would work out is to make a replacement for one of their generators (1/3 of total power needed) and take it from there. I’ve been looking online for where deals on good batteries, and wondering if a 12, 24 or 48v system makes sense.
Here’s my calculations: (happy to be corrected)
Working off 400 phones for 3 hours.
Assuming 2A charging from usb sockets:
5v x 2A (10W per phone)
each phone - 10W x 3 hrs = 30Wh per phone
30wh x 400 = 12kWh
Convert to 12v Ah: 12,000Wh ÷ 12V = 1000Ah
Convert to 24v Ah: 12,000Wh ÷ 24V = 500Ah
Convert to 48v Ah: 12,000Wh ÷ 48V = 250Ah
+10-15% for conversion and losses.
Continuous output:
Must support 400 x 10w = 4kw
So this would mean three roughly 4kwh modules, with 1.33kw continuous output.
Let me know what you think, and thanks again!
Sid